I need to wire a new outlet for our garbage disposal we are installing. There is a current switch next to the sink that only turns on one light over the sink.

Can I disconnect this light, re-route the wires done to a new GFCI plug for the Disposal for an on off outlet under the sink? Would any other wires need to be run? Or would all the wires from the light suffice? Essentially the outlet becomes the light. I would then re-route new wiring in the attic for the light over the sink to tie into another circuit.

Am I missing something?
Reply With Quote Quick reply to this message

 
Old 09-12-2015, 10:00 PM
 
Location: Riverside Ca
22,146 posts, read 33,537,436 times
Reputation: 35437
No don't do that. ( the reason is light wiring use a different size wire from a outlet and that size is not recommended for outlet use)
Is there a outlet below the sink? If there is that outlet should be a switched outlet. It's called a half hot in electrician speak.

Get a tester and see if the outlet is hot. If half works and half doesn't look for another switch or button somewhere.
Pull the light switch off the wall. Look and see if there is another set of wires that may be disconnected behind the switch, if there is pull the outlet see if there are wires discinbected behind there.Let me know if there are wires or a outlet


If there is no outlet.

Run another set of wires from the existing switch to the location of your disposal ( black red white green ) ask for 12/3 Romex at the hardware store. Get a cheap no touch tester too.

Buy a double wall switch that fits in a single gang box ( two switches that wil fit in the place if your old single switch.) and a outlet. A retro electrical box and some wire nuts. Make sure the outlet is 20 amp rated.

Let me know and I'll tell you how to wire it up so you have a light a working hot outlet and a switched outlet for the disposal.
Reply With Quote Quick reply to this message
 
Old 09-12-2015, 10:44 PM
 
Location: Johns Creek, GA
17,475 posts, read 66,054,754 times
Reputation: 23626
Well, if you have attic above and you're running new wire just run a new 20amp circuit (12awg)for the disposal.

Is there a dishwasher? Not a reccomendation, but you used to be able to run D/W&disosal on a 20amp circuit- corded&plugged.

If there isn't a D/W but there could be one in the future, run a 3/wire 12awg. You can have two different circuits but only have to run/fish the one "wire" instead of two separate ones.

Either way, do not do as you thought you could.

Also, the NEC has this little "catch phrase" in several codes- "...follow manufacturer's instructions for installation...". So, with that in mind what does the manufacturer recommend for a recepticle/circuit?

Last edited by K'ledgeBldr; 09-12-2015 at 11:22 PM..
Reply With Quote Quick reply to this message
 
Old 09-12-2015, 10:48 PM
 
Location: Riverside Ca
22,146 posts, read 33,537,436 times
Reputation: 35437
Running a new circuit is optimal but it's rarely easy to do. But if he has a dishwasher too it would be the best way.

Op can you post pics
Reply With Quote Quick reply to this message
 
Old 09-12-2015, 11:29 PM
 
153 posts, read 278,245 times
Reputation: 79
Ok. Let me elaborate.

There is a dedicated 20 amp fuse from the box that feeds a GFCI outlet for the dishwasher. This GFCI outlet stubs up to the light switch by the sink, from which it turns the light above the sink on/off. So the only thing on the circuit is the dishwasher outlet and the light above the sink.

I do not want this light above the sink on this circuit. I would like to keep the switch however and make that my garbage disposal switch. The wiring is already nice heavy 12 AWG wire. Can I make the GFCI dishwasher outlet have one outlet running all the time for the dishwasher and one outlet on/off via the switch for the disposal?

So now that the light above the sink is off of this circuit, how do I tie it into the rest of the lights in the kitchen?

I hope this makes sense, if not I can post a picture or diagram. Let me know.
Reply With Quote Quick reply to this message
 
Old 09-13-2015, 10:11 AM
 
Location: Johns Creek, GA
17,475 posts, read 66,054,754 times
Reputation: 23626
GFCI recepticles are made in such a way that you can not make one half switched.
You have line terminals and load terminals- "line" is power coming in; load would be for "additional" recepticles that you want GFCI protected.

But, in your scenario the GFCI is unwarranted. Remove the GFCI, replace it with a regular recepticle, break the tab on the "hot" side and run a switch leg to the switch box. Both wires are now "black"- if you would still want the GFCI protection change the breaker to a GFCI.

As for the light just run a 14awg from the Jbox of the light to a Jbox of another light- wht/wht, blk/blk, grd/grd.
Reply With Quote Quick reply to this message
 
Old 09-13-2015, 05:08 PM
 
153 posts, read 278,245 times
Reputation: 79
Quote:
Originally Posted by K'ledgeBldr View Post
GFCI recepticles are made in such a way that you can not make one half switched.
You have line terminals and load terminals- "line" is power coming in; load would be for "additional" recepticles that you want GFCI protected.

But, in your scenario the GFCI is unwarranted. Remove the GFCI, replace it with a regular recepticle, break the tab on the "hot" side and run a switch leg to the switch box. Both wires are now "black"- if you would still want the GFCI protection change the breaker to a GFCI.

As for the light just run a 14awg from the Jbox of the light to a Jbox of another light- wht/wht, blk/blk, grd/grd.
Thanks for the help. I will replace the GFCI. I just wired that in place because it made sense with water being so close. Before it was hard wired and linked to the switch as mentioned above. I can put a normal outlet in there and rip the tab off, I didn't think about the disposal on/off aspect until after the fact, hence why I cam on to this forum.

If anyone has anything else to add, it is welcome. Thanks again!
Reply With Quote Quick reply to this message
 
Old 09-13-2015, 08:34 PM
 
Location: Riverside Ca
22,146 posts, read 33,537,436 times
Reputation: 35437
Quote:
Originally Posted by K'ledgeBldr View Post
GFCI recepticles are made in such a way that you can not make one half switched.
You have line terminals and load terminals- "line" is power coming in; load would be for "additional" recepticles that you want GFCI protected.

But, in your scenario the GFCI is unwarranted. Remove the GFCI, replace it with a regular recepticle, break the tab on the "hot" side and run a switch leg to the switch box. Both wires are now "black"- if you would still want the GFCI protection change the breaker to a GFCI.

As for the light just run a 14awg from the Jbox of the light to a Jbox of another light- wht/wht, blk/blk, grd/grd.

This^^^
Reply With Quote Quick reply to this message
 
Old 09-14-2015, 11:33 AM
 
17,584 posts, read 15,259,939 times
Reputation: 22915
I found this, which I like a whole lot better than a normal switch and makes installation a snap..

InSinkErator SinkTop Switch - Single Outlet*| InSinkErator

Basically it's an air activated switch, so, you just plug it in, wire a normal plug to the disposal, and plug the disposal into this outlet.. Then run the air tubing up to the sink, pop the knockout out, put in the pushbutton air-switch.. No reaching to the wall.. Switch is right there beside the faucet. No additional wiring.

Not sure how it would work with GFCI, but.. I can't see any issues with it.
Reply With Quote Quick reply to this message
Please register to post and access all features of our very popular forum. It is free and quick. Over $68,000 in prizes has already been given out to active posters on our forum. Additional giveaways are planned.

Detailed information about all U.S. cities, counties, and zip codes on our site: City-data.com.


Reply
Please update this thread with any new information or opinions. This open thread is still read by thousands of people, so we encourage all additional points of view.

Quick Reply
Message:


Over $104,000 in prizes was already given out to active posters on our forum and additional giveaways are planned!

Go Back   City-Data Forum > General Forums > House

All times are GMT -6. The time now is 08:46 AM.

© 2005-2024, Advameg, Inc. · Please obey Forum Rules · Terms of Use and Privacy Policy · Bug Bounty

City-Data.com - Contact Us - Archive 1, 2, 3, 4, 5, 6, 7, 8, 9, 10, 11, 12, 13, 14, 15, 16, 17, 18, 19, 20, 21, 22, 23, 24, 25, 26, 27, 28, 29, 30, 31, 32, 33, 34, 35, 36, 37 - Top