Welcome to City-Data.com forum! Make sure to register - it's free and very quick! You have to register before you can post and participate in our discussions with 700,000 other registered members. User profiles and some forums can only be seen by registered members. After you create your free account you will be able to customize many options, you will have the full access to over 15,000 posts/day about local topics and you will see fewer ads.

Get a detailed profile
Search Forums  (Advanced)
Business Search - 14 Million verified businesses
Search for:  near: 
Reply


 
Old 07-20-2009, 10:31 AM
Senior Member
Status: "The Reckoning Resumes Dec. 12..." (set 18 days ago)
 
Join Date: Jan 2008
Location: Visitation between Wal-Mart & Home Depot
4,104 posts, read 2,738,757 times
Reputation: 2164
jimboburnsy has a reputation beyond repute
jimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond repute
Default 220v question...

Alright,

I have an old 220v outlet in my master bedroom (ran a window A/C unit in a former life) that I've been meaning to get around to for quite some time.

This is old, 8 guage stranded copper, ungrounded romex hooked up to a 40 amp tandem breaker.

I would like to remove the old tandem breaker, replace it with a pair of 15 amp breakers and install a 2-gang box with GFI (marked "no equipment ground", of course) in place of the old 220v outlet (this circuit was dedicated to the window unit, probably a retrofit).

I will be able to power each outlet with one leg of the 220v, but I will only have a single neutral. Is it possible for me to create a dangerous condition by having two outlets powered by separate circuits on a common neutral?

My other possibility (or maybe 'another' possibility) would be to simply cap one of the hot legs and piggyback both outlets, leaving an unused slot at the panel.

What's better?
Reply With Quote Quick reply to this message

 
Old 07-20-2009, 11:36 AM
Trolls hate me.
 
Join Date: Jul 2007
Location: West Michigan
7,441 posts, read 4,886,774 times
Reputation: 7694
Bydand has a reputation beyond reputeBydand has a reputation beyond reputeBydand has a reputation beyond reputeBydand has a reputation beyond repute
Bydand has a reputation beyond reputeBydand has a reputation beyond reputeBydand has a reputation beyond reputeBydand has a reputation beyond reputeBydand has a reputation beyond reputeBydand has a reputation beyond reputeBydand has a reputation beyond reputeBydand has a reputation beyond reputeBydand has a reputation beyond reputeBydand has a reputation beyond repute
Sharing a neutral won't work with two GFCI's usually. And the breaker would have to be a 2 pole breaker to break both sides of the circuit at the same time.
Reply With Quote Quick reply to this message
 
Old 07-20-2009, 11:51 AM
Senior Member
Status: "The Reckoning Resumes Dec. 12..." (set 18 days ago)
 
Join Date: Jan 2008
Location: Visitation between Wal-Mart & Home Depot
4,104 posts, read 2,738,757 times
Reputation: 2164
jimboburnsy has a reputation beyond repute
jimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond repute
Quote:
Originally Posted by Bydand View Post
Sharing a neutral won't work with two GFCI's usually. And the breaker would have to be a 2 pole breaker to break both sides of the circuit at the same time.
Good point about the GFI's, I hadn't considered that...

About the breaker, why would it be necessary to have both sides of the circuit broken at the same time if the hot legs are split into separate circuits?
Reply With Quote Quick reply to this message
 
Old 07-20-2009, 01:22 PM
Universal Supreme Dude
 
Join Date: Sep 2006
3,030 posts, read 4,104,997 times
Reputation: 1562
Cosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant future
Default Seeing if I understand this right.

You really want to use the old 220VAC wires to install two normal 115 VAC receptacles.

If so I would just disconnect it all in the panel. Do a standard three wire grounded installation using those wires. It could be ganged in the bedroom for as many outlets as you wish. The wire size is way over kill for any normal 115 VAC circuit. One of the receptacles in the bedroom (first one) could be a GFI, the others downstream protected by it.

Could even make the one circuit a 30 amp, put the right size breaker in the panel, have a spare slot. Just get all the parts sized / rated right for the circuit. Wire size sure will handle any load.
Reply With Quote Quick reply to this message
 
Old 07-20-2009, 02:25 PM
Senior Member
Status: "The Reckoning Resumes Dec. 12..." (set 18 days ago)
 
Join Date: Jan 2008
Location: Visitation between Wal-Mart & Home Depot
4,104 posts, read 2,738,757 times
Reputation: 2164
jimboburnsy has a reputation beyond repute
jimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond repute
Quote:
Originally Posted by Cosmic View Post
You really want to use the old 220VAC wires to install two normal 115 VAC receptacles.

If so I would just disconnect it all in the panel. Do a standard three wire grounded installation using those wires. It could be ganged in the bedroom for as many outlets as you wish. The wire size is way over kill for any normal 115 VAC circuit. One of the receptacles in the bedroom (first one) could be a GFI, the others downstream protected by it.

Could even make the one circuit a 30 amp, put the right size breaker in the panel, have a spare slot. Just get all the parts sized / rated right for the circuit. Wire size sure will handle any load.
Understanding check - You're saying I should re-purpose one of the wires as a ground? If so, I'm embarrassed that I didn't think of that.

Solves several problems.

In case I have an electrician poking around in there in the future, is marking the wire as "ground" with tape or a tag sufficient for the code? Also, If I don't have enough slack to get to the main grounding terminal, can I use a 12 guage jumper with wire nuts?
Reply With Quote Quick reply to this message
 
Old 07-20-2009, 02:45 PM
Universal Supreme Dude
 
Join Date: Sep 2006
3,030 posts, read 4,104,997 times
Reputation: 1562
Cosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant future
Default Just strip the ground wire..............

For the wire to be used as a ground just strip the insulation, it will be bare like all other ground wire. No real way to confuse what happened.

If you want just a 20 amp circuit, a #12 wire jumper to get to the ground bus should work, provided you put in a 20 amp breaker, same as any other 20 amp circuit.

I suppose you can use wire nuts in the panel. I don't like them. I might wrap the bigger wire with the #12 and solder it. Lots of places are quite anal about the subject of splices and where they occur / how it is done.

But everything considered should work for you.
Reply With Quote Quick reply to this message
 
Old 07-20-2009, 03:56 PM
Senior Member
Status: "The Reckoning Resumes Dec. 12..." (set 18 days ago)
 
Join Date: Jan 2008
Location: Visitation between Wal-Mart & Home Depot
4,104 posts, read 2,738,757 times
Reputation: 2164
jimboburnsy has a reputation beyond repute
jimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond repute
Quote:
Originally Posted by Cosmic View Post
For the wire to be used as a ground just strip the insulation, it will be bare like all other ground wire. No real way to confuse what happened.

If you want just a 20 amp circuit, a #12 wire jumper to get to the ground bus should work, provided you put in a 20 amp breaker, same as any other 20 amp circuit.

I suppose you can use wire nuts in the panel. I don't like them. I might wrap the bigger wire with the #12 and solder it. Lots of places are quite anal about the subject of splices and where they occur / how it is done.

But everything considered should work for you.
But if I wanted to go with a 30 amp breaker I would need #10?

If I solder it would I need a crimp or something to that effect?
Reply With Quote Quick reply to this message
 
Old 07-20-2009, 04:39 PM
Universal Supreme Dude
 
Join Date: Sep 2006
3,030 posts, read 4,104,997 times
Reputation: 1562
Cosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant futureCosmic has a brilliant future
Default Yep, #10 for 30 amp

Yeah you would go to #10 for that section of splice wire to go up to 30 amps.

You probably could do a crimp connector if you had one that big.

For the solder you normally just do a full wrap a bunch of times all way round and then maybe a bit of spiral out to the end.
Reply With Quote Quick reply to this message
 
Old 07-20-2009, 04:53 PM
Senior Member
Status: "The Reckoning Resumes Dec. 12..." (set 18 days ago)
 
Join Date: Jan 2008
Location: Visitation between Wal-Mart & Home Depot
4,104 posts, read 2,738,757 times
Reputation: 2164
jimboburnsy has a reputation beyond repute
jimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond reputejimboburnsy has a reputation beyond repute
Quote:
Originally Posted by Cosmic View Post
Yeah you would go to #10 for that section of splice wire to go up to 30 amps.

You probably could do a crimp connector if you had one that big.

For the solder you normally just do a full wrap a bunch of times all way round and then maybe a bit of spiral out to the end.
Cool.
Reply With Quote Quick reply to this message
 
Old 07-21-2009, 11:47 PM
Senior Member
 
Join Date: Oct 2008
Location: Valdosta, GA
1,053 posts, read 638,491 times
Reputation: 241
southgeorgia has a spectacular aura aboutsouthgeorgia has a spectacular aura aboutsouthgeorgia has a spectacular aura aboutsouthgeorgia has a spectacular aura aboutsouthgeorgia has a spectacular aura about
shared neutral works fine w/ two GFCI receps; you're working on the line side.

If you want GFCI protection at the panelboard, use a 2-pole GFCI.

Do not install a 30A circuit breaker unless you plan on using a 30A receptacle, which you cannot plug a standard 120V plug into.

You want to disconnect both lines simultaneously to protect you or someone else from inadvertently disconnecting the neutral at the buss w/ one line still hot.
Reply With Quote Quick reply to this message
Please register to post and access all features of our very popular forum. It is free and quick.

Detailed information about all U.S. cities, counties, and zip codes on our site: City-data.com.



Reply


Quick Reply
Message:

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Similar Threads


Go Back   City-Data Forum > General Forums > House

All times are GMT -6. The time now is 06:00 PM.

Copyright © 2005-2009, Advameg, Inc.

City-Data.com - Archive 1, 2, 3, 4, 5, 6, 7, 8, 9, 10, 11, 12, 13 - Top