Quote:
Originally Posted by tdstyles
Thanks so much I'll check it out. The temp is at 170 so that seems fine. I'll check the Aqua stat as you recommended when I get home tonight.
|
I'm assuming it's keeping up now that it's not -5 out?
Like I said it should be set at 180 hi and 160 for lo at this time of the year, at least. If you run into this problem again check the temperature on the boiler, if it's still in that range and the boiler is getting up to 180 or whatever you have the high set at then the boiler is making enough hot water and you can eliminate that as the issue.
From there for house that size you should have at least two zones and two pumps. If you have only one zone then you need to consider splitting it up. Zones can be created with independent pumps for each zone or with one pump and thermostatically controlled valves. If there is only one pump but you have valved zones then you should consider adding a pump. One nice thing about multiple pumps is if one breaks and you have cutoff valves before and after the pumps you can just shut them off to replace the bad pump and still have heat in the other zone.
Other things to look for is follow you pipes and see where they go, is there anywhere they are going through that is really cold?
One thing to keep in mind is that this was an unusual event, typically they try and size a boiler so it can meet the demands of that size house. You're boiler may be undersized for this type of cold but if it can keep up with whatever low temperatures are normal then there really isn't much you can do about it.