Quote:
Originally Posted by Squirl
Its an all electric house! Now I am thinking the cost savings isn't significant and the heat pump system is more expensive to buy. So, looks like I'll just do conventional forced air. Even thought its Texas, we do have about 10 days a year of below freezing weather and about 30 days below 45 degrees.
|
If you came to that conclusion, I'm not sure you understood the replies.
Example: Add 36K BTUs of heat into the house, outside temp is 40F
1) Electrical resistance heating: 100% efficient, takes 10.5 kwh of electricity
2) Heat pump: Assume COP of 3.7 @ 40F, takes around 2.9kwh of electricity to move 36k BTUs of energy from the outside to the inside
The heat pump uses nearly 4x less electricity to heat the house in this example.
When installed w/no gas furnace, it's typical to install a heat pump with electrical resistance panels inside the air handler for emergency heating. These would be used when:
1) Failure of heat pump condenser
2) Temperature so cold outside that heat pump cannot move heat into house fast enough to maintain setpoint
3) High temperature difference between setpoint and current temp, to help close gap faster. My thermostat does this (at our Las Vegas vacation house) when the delta is more than 2 degrees F. The only time this happens is when we turn the heat back on after the house has been empty and the thermostat was set to an away temperature of 55F. Other than that, I've never seen the heat strips kick in.