Quote:
Originally Posted by counterclockwise
If the 60 amp circuit breaker circuit feeds the unit through similar rated fuses in the pull out box why do the fuses never blow?
|
need the part number of the fuse if you want to see a comparison as to what will trip and at what point . .
i retired from the business but i still teach motor controls one day a week , so here is a very quick lesson on fuses and breakers :
the term slo-blow , time delay or dual element fuse only means that it has over current protection as well as short circuit protection .
over current means a slow rising curve that is above what should be drawn but no where near the currents of a short which can be explosive and devastating .
but the term slo-blo means nothing as far as the time curve . within those terms are all kinds of different slo-blo fuses .
in fact i used to do fuse co-ordination studies for my customers .
the difference in amperage between various amperage fuses has to be a certain span or you risk a short down stream on a branch taking out the larger power fuses up stream .
with standard time delay fuses like bussmans frn or frs you need at least 4x the sizes .
so if you have 800 amp fuses up stream , the next size tapped off for a branch has to be less than 200 amp fuses .
there are slo-blow time delay fuses that are called low peak fuses that allow 2:1 . so next stop would allow you a 400 amp switch .
so my point is the term slo-blow really means little as far as fuse time curves .
breakers and fuses will never match each other's curve regardless .one will always trip or blow sooner or later when it comes to over current .
when i design my control panels i use circuit breakers that are short circuit protection only. no motor over current protection at all .
standard breakers are called thermal magnetic.the thermal part refers to the action of the breaker due to motor over current and the magnetic part refers to it's short circuit ability. i use only magnetic trip breakers in my designs as i want the breakers to provide only short circuit protection , no over current protection .
i have overload blocks on my starters to protect the motors from over current . i don't want the breaker making its own determination as to when to trip because of over current because then you can get nuisance trips .
i carefully select the overload blocks to sustain either 500% overload for 10,20 or 30 seconds depending on the motor and application . a breaker has it's own built in time curve for over current that is different and non adjustable. some larger breakers can have the short circuit protection adjustable but not motor over current generally .
on the other hand if i am sizing standard time delay fuses i size them for 125% of the motor nameplate full load amperage .
so breakers and fuses are sized very differently .
sqd has a very good tutorial on the differences .
http://static.schneider-electric.us/...0600DB0601.pdf