Correct me if I'm wrong, but I thought that 14 gauge was only used for lights, and never for outlets.
That's wrong.
We use #14 for everything the code allows.
#12 is required for the kitchen counter receps, the dining room or adjacent nook to the kitchen, bathroom receptacles and you must have at least one 20A circuit (#12) in the laundry room for the washing machine. And of course for any fixed appliance that requires that size.
I run #14 for the fridge, dishwasher, icemaker, etc. . . unless I'm given specs beforehand that tell me the appliance needs a 20A circuit; the microwave can be on #14 but we use #12.
Also keep in mind any 20A circuits with only one device require a 20A device, not the economy grade 15A.
Everything else is fair game for #14; personally i think its foolish to waste the money on anything above it. And the labor for #14 is less than #12.
Location: Visitation between Wal-Mart & Home Depot
8,309 posts, read 38,766,834 times
Reputation: 7185
Quote:
Originally Posted by Bergenite
This is wrong. We just read that only kitchen outlets serving counters need GFCI protection.
That's actually not wrong at all. Since at least 2002 the NEC has required all 15A and 20A receptacles (with a few exceptions) in kitchens, bathrooms, ground level accessory buildings - whether finished or unfinished, basements, crawlspaces or outdoors - even if under the eave line, be GFCI protected.
That's actually not wrong at all. Since at least 2002 the NEC has required all 15A and 20A receptacles (with a few exceptions) in kitchens, bathrooms, ground level accessory buildings - whether finished or unfinished, basements, crawlspaces or outdoors - even if under the eave line, be GFCI protected.
Maybe I am reading the wrong book. But here's what the 2005 NEC says about the requirement for GFCI's in kitchens.
Article 210.8(A)6 Kitchens- Where the receptacles are installed to serve the countertop surfaces.
Has the 2008 version changed to include every outlet in the kitchen?
Location: Visitation between Wal-Mart & Home Depot
8,309 posts, read 38,766,834 times
Reputation: 7185
Quote:
Originally Posted by Bergenite
Maybe I am reading the wrong book. But here's what the 2005 NEC says about the requirement for GFCI's in kitchens.
Article 210.8(A)6 Kitchens- Where the receptacles are installed to serve the countertop surfaces.
Has the 2008 version changed to include every outlet in the kitchen?
Keep reading in 210.8(A).