Old 06-10-2010, 10:37 AM
 
1,963 posts, read 4,982,321 times
Reputation: 1456

Advertisements

Well, tech came out and didn`t know were the noise was coming from. This system has no belts or bearings so that wouldn`t be the problem. The only main things that the system has is the compressor and the motor. He said that the refrigerant deal was fine. He said that if there is a major problem with the unit, it will automatically shut itself off.

The high pitch noise happens after the unit has shut off completely.
Reply With Quote Quick reply to this message

 
Old 06-10-2010, 11:34 AM
 
Location: Bel Air, California
23,766 posts, read 29,048,781 times
Reputation: 37337
Quote:
Originally Posted by cl723 View Post
Well, tech came out and didn`t know were the noise was coming from. This system has no belts or bearings so that wouldn`t be the problem. The only main things that the system has is the compressor and the motor. He said that the refrigerant deal was fine. He said that if there is a major problem with the unit, it will automatically shut itself off.

The high pitch noise happens after the unit has shut off completely.
Great! those are the best kind of service calls for both you and the service tech. Could you describe the noise as if air escaping from a balloon that gets progressively quieter?
Reply With Quote Quick reply to this message
 
Old 06-10-2010, 12:19 PM
 
1,963 posts, read 4,982,321 times
Reputation: 1456
Yes, it`s like air escaping from a balloon but I`m not sure if it gets quieter.It might. I know that the noise is louder than it was last year.
Reply With Quote Quick reply to this message
 
Old 06-10-2010, 12:36 PM
 
Location: Bel Air, California
23,766 posts, read 29,048,781 times
Reputation: 37337
Quote:
Originally Posted by cl723 View Post
Yes, it`s like air escaping from a balloon but I`m not sure if it gets quieter.It might. I know that the noise is louder than it was last year.
I presume it eventually stops after a minute or two.
Reply With Quote Quick reply to this message
 
Old 06-10-2010, 12:38 PM
 
1,963 posts, read 4,982,321 times
Reputation: 1456
Yes, it does stop but I would say it lasts way less than a minute.
Reply With Quote Quick reply to this message
 
Old 06-10-2010, 01:31 PM
 
Location: Bel Air, California
23,766 posts, read 29,048,781 times
Reputation: 37337
If you are hearing this when the compressor stops (and only when your compressor stops) I go back to my earlier guess that you are hearing the high pressure refrigerant bleed back through the compressor valve(s) to the low pressure section of the compressor. It's normal for the system pressure to equalize but this generally happens in your evaporator section and would not be "heard". The valves are not unlike the reed in a kazoo and I think you are hearing one of them vibrating because it isn't completely sealing like it should.

Probably a small leak-by and not enough slop in the valves to affect system performance and something that wouldn't show up when the tech had his gauges on it while it was running. It might have shown up with the guages by observing how fast the pressures equalize upon shut-down but if it's cooling your house then I wouldn't worry about it.

The one potential problem is that it may be possible at some point to have liquid refrigerant (from the condensor) bleed past the valves into the compressor piston section during the off cycle. The compressor does not like to pump liquid and will likely destroy itself in attempting to do so at start up. This is called scrambling the compressor, cute huh?

Not sure what your observation of the squeal getting louder this year would imply. Don't worry tho, if yours hasn't destroyed itself by now, your leak (you aren't "losing" any refrigerant) is small enough that it probably won't happen anytime soon.

Or I could be completely wrong.

Stupid Air Conditioners.
Reply With Quote Quick reply to this message
 
Old 06-10-2010, 04:50 PM
 
1,963 posts, read 4,982,321 times
Reputation: 1456
Thanks for your help.
Reply With Quote Quick reply to this message
 
Old 07-01-2010, 10:00 PM
 
1 posts, read 15,632 times
Reputation: 10
I know its been a while, but have you solved this problem? I have a similar problem but only on startup for less than 25 seconds. Ive had 3 different companies come out and no one had any idea, as the ac is cooling fine. The last company thought it was the reversing valve and had it relplaced, but the sound is still there. Now we are waiting on a rep from the manufactuer to come out.
Reply With Quote Quick reply to this message
 
Old 07-25-2010, 08:36 PM
 
1 posts, read 15,540 times
Reputation: 10
every time i turn on my central air unit it shorts out at my circuit breaker
Reply With Quote Quick reply to this message
 
Old 07-25-2010, 08:54 PM
 
48,502 posts, read 96,848,488 times
Reputation: 18304
You need to call a technican as soemthing is overloading the breaker which is what its there for.
Reply With Quote Quick reply to this message
Please register to post and access all features of our very popular forum. It is free and quick. Over $68,000 in prizes has already been given out to active posters on our forum. Additional giveaways are planned.

Detailed information about all U.S. cities, counties, and zip codes on our site: City-data.com.


Reply
Please update this thread with any new information or opinions. This open thread is still read by thousands of people, so we encourage all additional points of view.

Quick Reply
Message:


Over $104,000 in prizes was already given out to active posters on our forum and additional giveaways are planned!

Go Back   City-Data Forum > General Forums > House

All times are GMT -6.

© 2005-2024, Advameg, Inc. · Please obey Forum Rules · Terms of Use and Privacy Policy · Bug Bounty

City-Data.com - Contact Us - Archive 1, 2, 3, 4, 5, 6, 7, 8, 9, 10, 11, 12, 13, 14, 15, 16, 17, 18, 19, 20, 21, 22, 23, 24, 25, 26, 27, 28, 29, 30, 31, 32, 33, 34, 35, 36, 37 - Top