I have been trying to replace a natural gas appliance and when I replaced it twice the pressure regulators on the new appliances would blow the release valve on the pressure regulators and then leak gas with two separate appliances with in a few weeks of each other.

When I called the gas company the call center said they would send a technician and I did not have to pay the 90.00 service fee if my appliance was not repaired.

The technician came over and tested the appliance and determined that the main valve was bad on my original appliance and the whole appliance had to be replaced. I asked them to test the pressure at the gas line that goes to the appliance and the technician just said I have a 2 pound gas regulator in my crawlspace and never tested to see what the actual pressure was at the gas line for the appliance.

I called the gas company again and they just said it was 7" water column for the gas line that was connected to the appliance then charged me the 90.00 service fee on my next gas bill even though the appliance was not repaired.

I then got a 0" to 10" water column natural gas manometer from a local store. Then I turned the gas off to the appliance and then plugged the rubber end of the manometer hose to the 1/8" inlet NPT tapping on the appliance being carful to make sure the needle stayed at zero after being connected. I turned the gas back on to the appliance and got 9" water column when the furnace was not running and when I tested it again it read 8" water column when the furnace was running.

The top of the gas regulator in the crawlspace says 2 pounds (55.56" water column) and steps that down to 7" water column or to 11" water column depending on what the regulator is set to so I am speculating that the main gas pressure regulator in the crawlspace is set to 8" and then when all gas appliances shut down the gas builds up by about 1" water column to the 9" water column reading.

Everyone says to call the gas company but when I say the gas company was not helpful they say to call a plumber.

Who should I call?

Can a licensed gas plumber adjust the main regulator inside the crawlspace or does the gas company have do this?

If I call a licensed gas plumber to adjust the gas pressure regulator and not the gas company can the plumber turn the main gas line off on the gas meter on the side of the house or does the gas company come over and turn it off?

I have a new Trane furnace and if the pressure on the main gas regulator was turned down to 7" water column it may affect this new furnace. Should I call the HVAC company that installed the furnace to check the gas pressure on the inlet NPT tapping on the furnace or could the same licensed gas plumber check the furnace?
Reply With Quote Quick reply to this message

 
Old 04-08-2018, 08:53 PM
 
4,164 posts, read 4,876,880 times
Reputation: 3931
I would call the gas company back again and be more persistent. They own the gas meter and the regulator, so they will have to replace it if there's a problem with too much pressure. This is a separate issue from the appliance itself which is why you might be spinning your wheels. The gas company is focusing on the appliance and not your meter, so when you call back don't talk about the appliance....just ask them to test your meter and regulator. Gas isn't something to mess around with or things can go boom.
Reply With Quote Quick reply to this message
 
Old 04-09-2018, 08:09 AM
 
270 posts, read 379,514 times
Reputation: 294
Sent this to my husband and this was his reply:

I am Sorry that you are having so much trouble. I hope this helps.

​9 inches of water column is not above the maximum allowable pressure on a gas appliance. I would not adjust it.

If you want to adjust it you can use your manometer to measure pressure as you turn the adjustment screw at the line regulator. Try 1 turn at a time (counter clockwise), release pressure at your manometer and check pressure. Set your pressure for 7 inches of water column static pressure (while appliance is not running). The pressure should drop to no less than 5 inches of water column while the appliance is running.

Does your appliance require an appliance regulator? Many, if not all gas cooktops require one that drops the pressure to 3.5 inches of water column. If it is required but not installed that could cause problems.

Usually turning off the gas meter is not necessary because the regulator should have a shut off valve in front of it. You own everything downstream of the gas meter, so the gas company does not need to be involved for anything beyond the meter. If you are deciding between a plumber & HVAC contractor, the HVAC contractor is more likely to be knowledgeable about gas.

One other thing, I suggest when turning on your shut off valves, do so slowly.


Good Luck!
Reply With Quote Quick reply to this message
Please register to post and access all features of our very popular forum. It is free and quick. Over $68,000 in prizes has already been given out to active posters on our forum. Additional giveaways are planned.

Detailed information about all U.S. cities, counties, and zip codes on our site: City-data.com.


Reply
Please update this thread with any new information or opinions. This open thread is still read by thousands of people, so we encourage all additional points of view.

Quick Reply
Message:


Settings
X
Data:
Loading data...
Based on 2000-2020 data
Loading data...

123
Hide US histogram

Over $104,000 in prizes was already given out to active posters on our forum and additional giveaways are planned!

Go Back   City-Data Forum > U.S. Forums > North Carolina > Raleigh, Durham, Chapel Hill, Cary

All times are GMT -6.

© 2005-2024, Advameg, Inc. · Please obey Forum Rules · Terms of Use and Privacy Policy · Bug Bounty

City-Data.com - Contact Us - Archive 1, 2, 3, 4, 5, 6, 7, 8, 9, 10, 11, 12, 13, 14, 15, 16, 17, 18, 19, 20, 21, 22, 23, 24, 25, 26, 27, 28, 29, 30, 31, 32, 33, 34, 35, 36, 37 - Top