Question about the plumbing vent. There is a plumbing vent already present for the utility sink and washer. Is it acceptable to tie into that for the toilet and sink in the bathroom we are building?
6' is the MAX for a toilet. And, a 2" vent is the bare minimum at that distance- but I'd do 3" if possible. The sink could run 3-1/2' with standard 1-1/2"; or go to 2" and it can run 5'.
Again, what size is the vent/drain you are looking to tap?
6' is the MAX for a toilet. And, a 2" vent is the bare minimum at that distance- but I'd do 3" if possible. The sink could run 3-1/2' with standard 1-1/2"; or go to 2" and it can run 5'.
Again, what size is the vent/drain you are looking to tap?
Although a lot of people do it, an AAR (air admittance valve) should not be used for a toilet!!! A lot of jurisdictions do not allow their use for a toilet. Think about what happens if the AAR fails!
Although a lot of people do it, an AAR (air admittance valve) should not be used for a toilet!!! A lot of jurisdictions do not allow their use for a toilet. Think about what happens if the AAR fails!
You get air suction through the toilet itself if it fails in the closed position. If it fails in the open position, you will may get sewer vapor/smell back flow into the area. In that case, you will smell it and simply replace the AAR with a new one. Been there done that and it is really no big deal. Takes maybe two minutes to replace one.