Also be aware that your generator can only supply 20.8 amps per leg CONTINIOUSLY (5000w total - 2500w/leg) - so don't load an individual leg up beyond that.
the 6250w is SURGE capacity.

Do you have any subpanels (garage/shop/wellpump)? that you need to turn breakers off on too, when testing?

Is the interlock properly requiring you to turn the MAIN breaker OFF before the generator breaker is moved to ON ?
The big breakers (range, W/H, A/C, furnace, dryer) get turned off and left off as well as the unconnected breakers. The 120v breakers connected to the generator are mainly just outlet and lights with the refrigerator being the biggest one. Everything is turned off to begin with and only the breakers that I want on are turned on.

Yes, the interlock requires me to turn off the main breaker before I can turn on the generator breaker.
Reply With Quote Quick reply to this message

 
Old 07-23-2023, 02:29 PM
 
Location: TEXAS
3,830 posts, read 1,385,293 times
Reputation: 2020
^ Seems if you got all that covered then it's either mis-wired or getting leak-back on the ground wire tripping the GFCI
Reply With Quote Quick reply to this message
 
Old 07-23-2023, 08:27 PM
 
516 posts, read 1,076,811 times
Reputation: 867
Quote:
Originally Posted by CCCyou View Post
^ Seems if you got all that covered then it's either mis-wired or getting leak-back on the ground wire tripping the GFCI

I think we already said that. Its connected via a breaker interlock, the neutral and ground are bonded at the service panel causing a GFCI trip.


The fix is to remove the bond at the generator since the one at the service is required to be there
Reply With Quote Quick reply to this message
 
Old 10-21-2023, 03:26 PM
 
2,718 posts, read 2,219,341 times
Reputation: 2820
WEN sent me another inverter for my generator. I changed it out and I am ready to test it on my house. It worked on my RV and powered two a/c units. The double pole 30 amp breaker right now has only one pole wired for 120. Can I just connect the other wire (wire nut off to the side) to the other pole? I don't want to pay for an electrician to come back out for 5 minutes of work. I will turn off all of the power at the pole before I do this.
Reply With Quote Quick reply to this message
Please register to post and access all features of our very popular forum. It is free and quick. Over $68,000 in prizes has already been given out to active posters on our forum. Additional giveaways are planned.

Detailed information about all U.S. cities, counties, and zip codes on our site: City-data.com.


Reply
Please update this thread with any new information or opinions. This open thread is still read by thousands of people, so we encourage all additional points of view.

Quick Reply
Message:


Over $104,000 in prizes was already given out to active posters on our forum and additional giveaways are planned!

Go Back   City-Data Forum > General Forums > House
Similar Threads

All times are GMT -6. The time now is 01:13 AM.

© 2005-2024, Advameg, Inc. · Please obey Forum Rules · Terms of Use and Privacy Policy · Bug Bounty

City-Data.com - Contact Us - Archive 1, 2, 3, 4, 5, 6, 7, 8, 9, 10, 11, 12, 13, 14, 15, 16, 17, 18, 19, 20, 21, 22, 23, 24, 25, 26, 27, 28, 29, 30, 31, 32, 33, 34, 35, 36, 37 - Top