...The condensation is from when the dryer is off...
|
Well, not necessarily. You're correct that warm, moist household air can still migrate up into the cold portion of the vent line when the dryer is off, condense, and run back down. Hence your comment on keeping the fan on all the time or getting a damper of some sort to close off the vent line.
However, if the line is uninsulated and extends through a cold attic space, if its chilly enough condensation will occur even when the dryer is operating and the condensate will flow back down the vent line - particularly if it's a vertical line to the roof.
So, we're back to relocating the line or making sure it runs on the "warm" side of the insulation up to the point it immediately vents outside. If the line is on the "warm side" of things all the way to the outside vent and there's still condensation, then the run is just way too long. In that instance the booster fan may work, but why use more electricity, have a piece of equipment that can fail, and the possibility of flammable lint building up on an electric fan? Either properly insulate the vent line or reroute it so it exits the house in as short a distance as possible.
You know, if appliance installers, builders, and "scorched air" HVAC guys had ever worked with steam heating systems, they'd know how to run dryer vents so there wouldn't be this problem!