The fan on my Trane outside air conditioning unit is always running. The house stays nice and cool but the fan doesn't turn off even when I turn off the a/c. The only way to stop it is when I flip off the power at the breaker box.

When the a/c is off the fan spins but not too fast, it does goes fast when the a/c is running.

Anyone else see this problem before? Any suggestions on how to self fix or do I need a repairman?

Thanks.
Reply With Quote Quick reply to this message

 
Old 07-07-2009, 02:47 PM
 
1,009 posts, read 4,039,173 times
Reputation: 760
A defective contactor is one candidate.






YouTube - Residential HVAC Contactors Part One
Reply With Quote Quick reply to this message
 
Old 07-07-2009, 05:28 PM
 
23,601 posts, read 70,425,146 times
Reputation: 49277
Those pics look like an old Potter Brumfeld contactor/relay. Dunno why they always had a tendency to fuse contacts together, but that was a given.
Reply With Quote Quick reply to this message
 
Old 07-08-2009, 08:10 AM
 
41 posts, read 559,096 times
Reputation: 50
Where are those contactor's located?

Also, once I locate them, will I be able to tell if that is the problem by seeing if they move or are stuck? If not what should I look for?

Thanks for your help.


Sorry if I should have posted this in the big a/c repair thread instead. You guys have helped a lot of people on this site!!!!
Reply With Quote Quick reply to this message
 
Old 07-08-2009, 10:38 AM
 
1,009 posts, read 4,039,173 times
Reputation: 760
Quote:
Originally Posted by cgar22 View Post
what should I look for?
Your queries reflect that you are NOT taking the initiative to do Google and YouTube research. Pretty much 2 types of internet users . . searchers and slackers. The latter tend to seek out others to exploit with endless questions.

Might start with an advanced search on trane.com . . example.
Reply With Quote Quick reply to this message
 
Old 07-08-2009, 11:40 AM
 
41 posts, read 559,096 times
Reputation: 50
While I didn't do I search on contactor's, I have been doing extensive searches during the last two weeks trying to find others with a similiar problem. I have only seen the fan always running problem in one or two other places so I guess it isn't very common. Hopefully once I have it fixed, I can document everything and it will be easier for others later.
Reply With Quote Quick reply to this message
 
Old 07-08-2009, 01:36 PM
 
23,601 posts, read 70,425,146 times
Reputation: 49277
I've mentioned a similar type of problem a couple or three times here in this forum. Guess you can limit your search.
Reply With Quote Quick reply to this message
 
Old 07-09-2009, 12:34 AM
 
29,939 posts, read 39,468,904 times
Reputation: 4799
It doesn't always mean it's the contactor. You could have a compressor problem where it cuts off and the contactor is staying closed because the thermostat is still calling for cooling. Compressors have overloads which cut out the compressor at 71% of the locked rotor amperage. I know you said it doesn't cut off even when you cut off the unit. Just a heads up.

Last edited by BigJon3475; 07-09-2009 at 12:45 AM..
Reply With Quote Quick reply to this message
 
Old 07-09-2009, 07:48 AM
 
Location: NH. NY. SC. next move, my ground condo
3,533 posts, read 12,306,149 times
Reputation: 4520
the fan should run when the unit is running , right ?
Reply With Quote Quick reply to this message
 
Old 07-09-2009, 12:51 PM
 
29,939 posts, read 39,468,904 times
Reputation: 4799
Yes. You should hear a slight hum from the compressor and the air coming off the unit should be warmer than the ambient air entering it. If it's a multiple stage unit it will increase fan speeds to compensate for the compressor kicking into higher speeds. If the air coming off the top or side of the unit (side meaning a unit like a ductless mini-split) is the same temperature that's going into it either the inside air temp is extremely cold or the compressor isn't running.
Reply With Quote Quick reply to this message
Please register to post and access all features of our very popular forum. It is free and quick. Over $68,000 in prizes has already been given out to active posters on our forum. Additional giveaways are planned.

Detailed information about all U.S. cities, counties, and zip codes on our site: City-data.com.


Reply
Please update this thread with any new information or opinions. This open thread is still read by thousands of people, so we encourage all additional points of view.

Quick Reply
Message:

Over $104,000 in prizes was already given out to active posters on our forum and additional giveaways are planned!

Go Back   City-Data Forum > General Forums > House
Similar Threads

All times are GMT -6.

© 2005-2024, Advameg, Inc. · Please obey Forum Rules · Terms of Use and Privacy Policy · Bug Bounty

City-Data.com - Contact Us - Archive 1, 2, 3, 4, 5, 6, 7, 8, 9, 10, 11, 12, 13, 14, 15, 16, 17, 18, 19, 20, 21, 22, 23, 24, 25, 26, 27, 28, 29, 30, 31, 32, 33, 34, 35, 36, 37 - Top