Old 05-21-2017, 03:44 PM
 
Location: Sarasota FL
6,864 posts, read 12,091,244 times
Reputation: 6744

Advertisements

1998 unit- Goodman CPKJ30/Janitrol A32-05 newer stat Robertshaw 9725i2
Screen went blank. Removed stat face. No volts at C and R terminals. Both terminals on transformer show about 4 volts but not at C and R ?. But three leads at defrost PCB on condenser are about 10 volts each. [which includes C, Y, O]
Bad transformer or PCB?
Reply With Quote Quick reply to this message

 
Old 05-21-2017, 03:54 PM
 
Location: A blue island in the Piedmont
34,111 posts, read 83,064,731 times
Reputation: 43697
Quote:
Originally Posted by d4g4m View Post
No volts at C and R terminals.
Check the transformer down at the furnace and see what the R & C show.
And of course the 120V input too.

Quote:
Bad transformer...?
It happens
Reply With Quote Quick reply to this message
 
Old 05-21-2017, 06:08 PM
 
Location: Sarasota FL
6,864 posts, read 12,091,244 times
Reputation: 6744
^^^^
System is split heat pump [compressor/air handler] not a furnace. And only one transformer in air handler
Input to transformer is 240V [reads 252V]
Reply With Quote Quick reply to this message
 
Old 05-21-2017, 06:55 PM
 
Location: A blue island in the Piedmont
34,111 posts, read 83,064,731 times
Reputation: 43697
Quote:
Originally Posted by d4g4m View Post
Input to transformer is 240V [reads 252V]
And the output from the X-former?
Reply With Quote Quick reply to this message
 
Old 05-22-2017, 07:02 PM
 
Location: Sarasota FL
6,864 posts, read 12,091,244 times
Reputation: 6744
^^^^
output on both [24V] terminals is around 8V and it is not 8V at 'R' term on stat. It's zero.
Reply With Quote Quick reply to this message
 
Old 05-22-2017, 07:29 PM
 
Location: WMHT
4,570 posts, read 5,681,797 times
Reputation: 6761
Disconnect transformer from load, if the output still reads less than 24VAC, the transformer is bad.
Reply With Quote Quick reply to this message
 
Old 05-23-2017, 07:40 PM
 
Location: Sarasota FL
6,864 posts, read 12,091,244 times
Reputation: 6744
^^^^^
Removed transformer. Did an OHM test. 24v side shows .9 ohm. 240v side shows open [nothing] Transformer is bad and will be replaced. Research shows that .9 is normal and should be same on both sides.
But what I find odd is that even though the 240v side doesn't show a resistance, I can get low volt reading [4 volts] from wires throughout the system. I think there is some volts going into and through the transformer but not enough to get an ohm reading.
Reply With Quote Quick reply to this message
 
Old 05-24-2017, 08:42 AM
 
Location: WMHT
4,570 posts, read 5,681,797 times
Reputation: 6761
Four volts is low enough to just be a phantom.

Look for a transformer that has an accessible fuse (e.g. a automotive blade-type) on the secondary, or at least a self-resetting (PTC) fuse. You can also put a fuse or breaker on the primary, but that isn't normally necessary.
Reply With Quote Quick reply to this message
 
Old 05-24-2017, 03:58 PM
 
621 posts, read 1,125,698 times
Reputation: 808
An open primary? That's not common at all and the control voltage would be -0- to grounded reference anywhere you check if the primary is open.

The primary for a 240/24 step down transformer should be 10 X the secondary resistance.

Are you sure you don't have a blown control voltage fuse somewhere that you've overlooked?

Last edited by btuhack; 05-24-2017 at 04:12 PM..
Reply With Quote Quick reply to this message
 
Old 05-24-2017, 06:43 PM
 
Location: Sarasota FL
6,864 posts, read 12,091,244 times
Reputation: 6744
^^^^^
There are no fuses in the air handler or on the outside condenser where 24V connects to defrost PCB or 240v connects to contactor/compressor/fan. There is a 240v fuse box attached to the house wall for compressor shut off service work. [besides the compressor and air handler breaker fuses in the garage panel] In any case, I found an exact transformer replacement from an ebay seller.
Reply With Quote Quick reply to this message
Please register to post and access all features of our very popular forum. It is free and quick. Over $68,000 in prizes has already been given out to active posters on our forum. Additional giveaways are planned.

Detailed information about all U.S. cities, counties, and zip codes on our site: City-data.com.


Reply
Please update this thread with any new information or opinions. This open thread is still read by thousands of people, so we encourage all additional points of view.

Quick Reply
Message:


Over $104,000 in prizes was already given out to active posters on our forum and additional giveaways are planned!

Go Back   City-Data Forum > General Forums > House

All times are GMT -6. The time now is 08:40 PM.

© 2005-2024, Advameg, Inc. · Please obey Forum Rules · Terms of Use and Privacy Policy · Bug Bounty

City-Data.com - Contact Us - Archive 1, 2, 3, 4, 5, 6, 7, 8, 9, 10, 11, 12, 13, 14, 15, 16, 17, 18, 19, 20, 21, 22, 23, 24, 25, 26, 27, 28, 29, 30, 31, 32, 33, 34, 35, 36, 37 - Top