Originally Posted by desertsun41 View Post
No a 15A and 20A are not equal. If they were then they wouldn't have different ratings.
"BTW, a 15 and 20 amp receptacle are electrically equally capable."

In other words, what satx56 is saying is that the 15A GFCIs are designed for 20A pass-through, which is indeed the case for the ones that I've encountered (P&S and Leviton).
Reply With Quote Quick reply to this message

 
Old 01-26-2010, 09:57 AM
 
Location: Pomona
1,955 posts, read 10,991,854 times
Reputation: 1562
Quote:
Originally Posted by PokerMunkee View Post
Ran into a snag. The fridge is the last on a string of 3 outlets.

[breaker]----<appliance outlet 1>-----<appliance outlet 2>----<fridge outlet>.
From the breaker, connect those wires to the LINE on a 15A GFCI (#1).
Connect the wires to #2 off the same LINE terminals, as so it will pass through without being protected. Nothing is to be connected on the load side.

#2 ... same thing - both sets of wires on the LINE.

#3 (fridge) ... a regular outlet connected as usual. This will be unprotected.

Any issues on #1 or #2, it'll be that specific GFCI that trips; No other outlet will be affected.
Reply With Quote Quick reply to this message
 
Old 01-26-2010, 10:19 AM
 
Location: Sherwood, OR
666 posts, read 1,845,734 times
Reputation: 679
Quote:
Originally Posted by Narfcake View Post
"BTW, a 15 and 20 amp receptacle are electrically equally capable."

In other words, what satx56 is saying is that the 15A GFCIs are designed for 20A pass-through, which is indeed the case for the ones that I've encountered (P&S and Leviton).
...and that matches 210.21(B)(3) in the 2008 NEC which states:

(3) Receptacle Ratings.
Where connected to a branch circuit supplying two or more receptacles or outlets, receptacle ratings shall conform to the values listed in Table 210.21(B)(3), or where larger than 50 amperes, the receptacle rating shall not be less than the branch-circuit rating.

Table 210.21(B)(3) shows that a 20a circuit can use 15a or 20a receptacles. Since most installed receptacles are duplex, one receptacle qualifies it. If you had a single outlet receptacle by itself on a branch circuit, it would have to be rated at no less than the amperage of the circuit.
Reply With Quote Quick reply to this message
 
Old 01-26-2010, 02:20 PM
 
Location: South Central Texas
114,838 posts, read 65,921,881 times
Reputation: 166935
Guys all I'm saying is that 15 and 20 amp duplex or single receptacles appear to be same capacity. Break one of each open and you'll see what I mean. These may be the only two 115V devices rated differently that this is true for. The difference is the 20 amp has a T slot and should have no less than # 12 wire to it. An appliance needing a 20 amp circuit will plug into the 20 but not the 15 amp receptacle. The 15 amp receptacle is apparently actually good for 20 amps also. If fed by #12 wire and not #14. Same is true for 220 receptacles . Break open a 15 Tandem and a 20 amp T Tandem ...no difference in metal gauges. Now as far as GFI's in series or so on I won't comment. I've done considerable electrical stuff as an A/C technician. I've done quite a bit of many things. BTW, If you compare 30 amp and 50 amp receptacles there may be a considerable difference.
Reply With Quote Quick reply to this message
 
Old 01-26-2010, 04:27 PM
 
Location: South Central Texas
114,838 posts, read 65,921,881 times
Reputation: 166935
Quote:
Originally Posted by satx56 View Post
Guys all I'm saying is that 15 and 20 amp duplex or single receptacles appear to be same capacity. Break one of each open and you'll see what I mean. These may be the only two 115V devices rated differently that this is true for. The difference is the 20 amp has a T slot and should have no less than # 12 wire to it. An appliance needing a 20 amp circuit will plug into the 20 but not the 15 amp receptacle. The 15 amp receptacle is apparently actually good for 20 amps also. If fed by #12 wire and not #14. Same is true for 220 receptacles . Break open a 15 Tandem and a 20 amp T Tandem ...no difference in metal gauges. Now as far as GFI's in series or so on I won't comment. I've done considerable electrical stuff as an A/C technician. I've done quite a bit of many things. BTW, If you compare 30 amp and 50 amp receptacles there may be a considerable difference.
Perhaps more plainly stated this way. The devices are rated as to minimum current carrying ability. It is the configuration of it's slots which allow/deny acceptance of certain appliance plugs. If it's rated at 20 amps it will accept a 15 or 20 amp plug. If it's rated at 15 amps it will only accept a 15 amp plug. Configuration shows a circuits current carrying capacity. You wouldn't put a 20 amp device on a 14 gauge circuit. 15 amp device on a 12 gauge circuit is fine. Actually you should know there isn't much difference in large 220 receptacles aside from Ground/neutral prong the other blades may be the same size!! Check out a 25 amp and 30 amp dryer, 50 amp range/welder receptacle.
Reply With Quote Quick reply to this message
 
Old 05-09-2013, 09:22 AM
 
1 posts, read 3,939 times
Reputation: 10
Actually devices are rated for it's maximum capacity. While they may seen similar in construction it is recommended to use it as intended. I.e. for a single branch 20A 1500 VA countertop outlet install a 20A gfci. Some state AHJs would fail you for installing a single 15A. But for branches with more than one outlet it is ok to use 15A because i.e. 2x15A = 30A (where you would never draw that much).
Reply With Quote Quick reply to this message
 
Old 05-09-2013, 09:55 AM
 
Location: A blue island in the Piedmont
34,123 posts, read 83,117,043 times
Reputation: 43712
Quote:
Originally Posted by fastx21 View Post
But for branches with more than one outlet...
Kitchens are required to have no less than TWO 20Amp Small Appliance Circuits...
protected for load (amps) by 20A circuit breakers.

These circuits require no less than two GFC-I receptacles (the first on the circuit) but
all subsequent receptacles (of any number) can be regular receptacles. 15A devices are fine.

Similar applies for AFCI and other circuits.
Unless it's dedicated (like a sump pump) a 20A circuit can use 15A devices.
Reply With Quote Quick reply to this message
 
Old 05-09-2013, 11:24 AM
 
Location: Grosse Ile Michigan
30,708 posts, read 79,922,272 times
Reputation: 39459
Instead of GFCI receptacles, you can use a gfci breaker to protect the entire circuit. However that is pretty dumb IMO because, if it trips, you have to run to the breaker box to reset it.
Reply With Quote Quick reply to this message
Please register to post and access all features of our very popular forum. It is free and quick. Over $68,000 in prizes has already been given out to active posters on our forum. Additional giveaways are planned.

Detailed information about all U.S. cities, counties, and zip codes on our site: City-data.com.


Reply
Please update this thread with any new information or opinions. This open thread is still read by thousands of people, so we encourage all additional points of view.

Quick Reply
Message:


Over $104,000 in prizes was already given out to active posters on our forum and additional giveaways are planned!

Go Back   City-Data Forum > General Forums > House

All times are GMT -6. The time now is 03:39 AM.

© 2005-2024, Advameg, Inc. · Please obey Forum Rules · Terms of Use and Privacy Policy · Bug Bounty

City-Data.com - Contact Us - Archive 1, 2, 3, 4, 5, 6, 7, 8, 9, 10, 11, 12, 13, 14, 15, 16, 17, 18, 19, 20, 21, 22, 23, 24, 25, 26, 27, 28, 29, 30, 31, 32, 33, 34, 35, 36, 37 - Top