I moved into a new apartment this month, which is supposed to be luxury. HVAC unti from Islandaire is there in living and bedroom. Building boiler heat is not continuous and works in intervals. When boiler is working and I have heating button ON, I notice that heat is dispensed with a light speed fan and the fan and heating eventually stops when boiler goes off, it kicks back-in again sooner boiler is working again.
Now the issue, Bed room unit fan never stops when heat button is ON. It is fast & noisy as well. When boiler stops it keeps, bedroom unit throwing cold air. I don't wish to baby sit this. I wanted to check if any of you have experienced similar situation? I explained this to bldg super and he says it is working as expected. I plan to reach out to bldg mgmt but likes to be prepared with the correct info.
Should I have some A/c repair person check this? or there is anyway I can check? What is your suggestion to approach this issue?
Reply With Quote Quick reply to this message

 
Old 11-30-2016, 10:24 AM
 
650 posts, read 2,518,387 times
Reputation: 299
It sounds like you have a PTAC? I have heard of one case where they are supplied by a master boiler in the basement (which only provides hot water to the PTAC) - any others are standalone units not connected to any common building mechanicals.

How do you know the boiler is on or off? Historically the vast majority of problems lie with the PTAC itself. I assume your lease covers who is liable for what in this regards.
Perhaps check with a neighbor or two if they are having a similar issue.
Reply With Quote Quick reply to this message
 
Old 11-30-2016, 12:37 PM
 
8 posts, read 23,357 times
Reputation: 11
thanks for the response. Yes it is PTAC unit. yes, the boiler is located at basement. When boiler is ON both units emits the hot air, when it gets Off I see living room heating fan stops and bed room one still running. Is this the right behavior? Should fan not stop when the boiler shuts down? There may be something wrong with the thermostat. Attaching an image for identifying the unit.

Thanks for the suggestion, I will check with my neighbors. Still have to meet people as moved in two weeks ago. In my lease all this lies with building to fix.
Attached Thumbnails
Need suggestion: Heating unit Issue in rented Apartment-img_2399.jpg  
Reply With Quote Quick reply to this message
 
Old 01-25-2017, 08:54 AM
 
Location: East Setauket
7 posts, read 76,671 times
Reputation: 29
Hello Namesake78,
Based on your info it sounds as if the aquastat has fallen off the heat pipe or has become disconnected from the unit. The photo below shows what the aquastat is. It needs to be clicked on to the heat pipe and plugged in to the molex plug with yellow wires. If it is already on the pipe and plugged in, chances are it needs a replacement. Please feel free to call our tech support at (800) 886-2759 and use extension 1148 for a walk through and further explanation.


Sincerely,
Islandaire Support
Reply With Quote Quick reply to this message
Please register to post and access all features of our very popular forum. It is free and quick. Over $68,000 in prizes has already been given out to active posters on our forum. Additional giveaways are planned.

Detailed information about all U.S. cities, counties, and zip codes on our site: City-data.com.


Reply
Please update this thread with any new information or opinions. This open thread is still read by thousands of people, so we encourage all additional points of view.

Quick Reply
Message:


Settings
X
Data:
Loading data...
Based on 2000-2020 data
Loading data...

123
Hide US histogram


Over $104,000 in prizes was already given out to active posters on our forum and additional giveaways are planned!

Go Back   City-Data Forum > U.S. Forums > New York > New York City

All times are GMT -6. The time now is 11:35 PM.

© 2005-2024, Advameg, Inc. · Please obey Forum Rules · Terms of Use and Privacy Policy · Bug Bounty

City-Data.com - Contact Us - Archive 1, 2, 3, 4, 5, 6, 7, 8, 9, 10, 11, 12, 13, 14, 15, 16, 17, 18, 19, 20, 21, 22, 23, 24, 25, 26, 27, 28, 29, 30, 31, 32, 33, 34, 35, 36, 37 - Top